1867687 Members
1692 Online
110514 Solutions
New Discussion

Re: P Class power issues

 
Nigel Peirce
Occasional Contributor

P Class power issues

We have five P-Class enclosures fed from a bus bar powered by two 3Phase power enclosures, each enclosure has six power supplies.

When running on a single power feed (Normally 3 phase) the right hand blades in our enclosures do not power back on without manual override. The Error Logs have messages to suggest the power supply is not redundant.
I have checked the power usage using the serial interface on the power enclosures and all 12 are averaging between 450-650 Watts each.
Each Power enclosure reports that "Enclosure Power Used: 3621W" & "Zone Power Allocated: 11804W", I am unsure what the Zone Power figure means!
All PSU show their status as "Present - Power Good"
Can anyone give advice on how to overcome this issue of them not automatically powering back on.
4 REPLIES 4
Nigel Peirce
Occasional Contributor

Re: P Class power issues

Forgot to mention that all enclosures have Firmware V2.33 & blades are running V1.91
Pasquino
Occasional Advisor

Re: P Class power issues

Hi,

is the load balancing cable installed?
Do you have a G1 or G2 enclosure?
Pasquino.
Nigel Peirce
Occasional Contributor

Re: P Class power issues

Yes the load balancing cable is installed and we have two G1 enclosures and three G2 enclosures.
Veram_
Frequent Advisor