- Community Home
- >
- Servers and Operating Systems
- >
- HPE ProLiant
- >
- Servers - General
- >
- Rack & Power Manager - Segment shutdown problem
Servers - General
1753889
Members
7635
Online
108809
Solutions
Forums
Categories
Company
Local Language
юдл
back
Forums
Discussions
Forums
- Data Protection and Retention
- Entry Storage Systems
- Legacy
- Midrange and Enterprise Storage
- Storage Networking
- HPE Nimble Storage
Discussions
Discussions
Discussions
Forums
Forums
Discussions
юдл
back
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
- BladeSystem Infrastructure and Application Solutions
- Appliance Servers
- Alpha Servers
- BackOffice Products
- Internet Products
- HPE 9000 and HPE e3000 Servers
- Networking
- Netservers
- Secure OS Software for Linux
- Server Management (Insight Manager 7)
- Windows Server 2003
- Operating System - Tru64 Unix
- ProLiant Deployment and Provisioning
- Linux-Based Community / Regional
- Microsoft System Center Integration
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Blogs
Information
Community
Resources
Community Language
Language
Forums
Blogs
Topic Options
- Subscribe to RSS Feed
- Mark Topic as New
- Mark Topic as Read
- Float this Topic for Current User
- Bookmark
- Subscribe
- Printer Friendly Page
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО07-13-2004 08:11 PM
тАО07-13-2004 08:11 PM
Rack & Power Manager - Segment shutdown problem
This is a bit complex, but bear with it...
I have 2 R3000 XR UPS configured in redundant config, currently powering 4 Windows Server 2003 servers. Each server has dual PSUs, each of which is fed from a different UPS thus ensuring reliability. Two of the servers are connected to a UPS via a serial cable for management purposes.
I have installed and configured RPM with the appropriate agents running on the appropriate servers. I have configured 3 of the server agents on load segment 1 of each UPS and set them up to run for 30 minutes before shutting down gracefully and removing power to the segment.
The problem is that is I remove utility power from one of the UPS (doesn't matter which), the RPM software immediately shuts off power to Segment 1 (it does not remove power from the other two segments) and the power remains off until I restore utility power back to the UPS, wherein it waits for 5 minutes (as configured by me) and then restores power.
This sounds very wrong to me, but I cannot work out where I am going wrong and, to be honest, it rather looks like a bug to me.
Any suggestions?
I have 2 R3000 XR UPS configured in redundant config, currently powering 4 Windows Server 2003 servers. Each server has dual PSUs, each of which is fed from a different UPS thus ensuring reliability. Two of the servers are connected to a UPS via a serial cable for management purposes.
I have installed and configured RPM with the appropriate agents running on the appropriate servers. I have configured 3 of the server agents on load segment 1 of each UPS and set them up to run for 30 minutes before shutting down gracefully and removing power to the segment.
The problem is that is I remove utility power from one of the UPS (doesn't matter which), the RPM software immediately shuts off power to Segment 1 (it does not remove power from the other two segments) and the power remains off until I restore utility power back to the UPS, wherein it waits for 5 minutes (as configured by me) and then restores power.
This sounds very wrong to me, but I cannot work out where I am going wrong and, to be honest, it rather looks like a bug to me.
Any suggestions?
- Tags:
- UPS
3 REPLIES 3
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО09-17-2004 07:29 AM
тАО09-17-2004 07:29 AM
Re: Rack & Power Manager - Segment shutdown problem
Stuart
You say "Two of the servers are connected to a UPS via a serial cable for management purposes". I assume that means you have two HP Rack and Power Management Servers running as well??? If so, this is a Bad thing. You should have only one Management server for this configuration.
Are there computers configured on load segments 2 & 3? If so what are there run times set to.
Bill
You say "Two of the servers are connected to a UPS via a serial cable for management purposes". I assume that means you have two HP Rack and Power Management Servers running as well??? If so, this is a Bad thing. You should have only one Management server for this configuration.
Are there computers configured on load segments 2 & 3? If so what are there run times set to.
Bill
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО03-01-2005 08:29 AM
тАО03-01-2005 08:29 AM
Re: Rack & Power Manager - Segment shutdown problem
I am having the same problem.
Any fix?
Any fix?
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО03-24-2005 12:45 AM
тАО03-24-2005 12:45 AM
Re: Rack & Power Manager - Segment shutdown problem
Stewart, the way HPRPM is designed to work in a redundant configuration is the HPRPM will turn off all load segments and the UPS if the Management Server detects that all attached servers are protected by another UPS. It sounds like all of the servers that are associated with load segmet (LS) 1 are associated with another UPS. That would explain why LS1 is turning off emidatly. Now regarding load LS 2 &3. You say that you have 4 servers attached to 2 UPSs 3 on LS1 of both UPSs. I assume that the 4th is on LS2. Assuming that the 4th server is on LS2: You also say that LS2 is not turning off like LS1. I would recomend that you check that the server on LS2 is associated with both UPSs. If the Management Server does not detect that it is associated with 2 UPS's it will not turn off that LS. If you have it associated with 2 UPS then I would check the Power fail settings for LS2. Make sure it is not set to infinate. Infinate should override all runtime settings.