can someone check my settings,  we've had power outages and the UPS has worked fine,  then power is restored and we can relax,   then suddenly few hours later the UPS turns off output power, then turns it back on,  for no reason, or we have a setting wrong

UPS Load Segment 1 shutdown is activated, 

why doesnt this clear when power is back?

anyone able to help?

 

he is the log,

2016/03/02 15:49:27 UPS Input AC Not Present
2016/03/02 15:49:27 UPS Input AC Under Voltage
2016/03/02 15:49:31 UPS On Battery
2016/03/02 15:49:34 Entire UPS shutdown is activated
2016/03/02 15:49:34 UPS Load Segment 1 shutdown is activated
2016/03/02 15:49:34 UPS Load Segment 2 shutdown is activated
2016/03/02 15:49:37 UPS On Battery Cleared
2016/03/02 15:49:41 UPS Input AC Not Present Cleared
2016/03/02 15:49:41 UPS Input AC Under Voltage Cleared
2016/03/02 16:23:02 UPS On Battery
2016/03/02 16:23:03 UPS Input AC Not Present
2016/03/02 16:23:03 UPS Input AC Under Voltage
2016/03/02 16:23:17 UPS On Battery Cleared
2016/03/02 16:23:19 UPS Input AC Not Present Cleared
2016/03/02 16:23:19 UPS Input AC Under Voltage Cleared
2016/03/02 16:29:44 UPS On Battery
2016/03/02 16:29:46 UPS Input AC Not Present
2016/03/02 16:29:46 UPS Input AC Under Voltage
2016/03/02 16:29:54 UPS On Battery Cleared
2016/03/02 16:30:01 UPS Input AC Not Present Cleared
2016/03/02 16:30:01 UPS Input AC Under Voltage Cleared
2016/03/02 18:36:14 UPS Load Segment 1 Is Off
2016/03/02 18:36:14 UPS Load Segment 2 Is Off
2016/03/02 18:36:15 UPS Output Is Off
2016/03/02 18:36:24 UPS Load Segment 1 Is On
2016/03/02 18:36:24 UPS Load Segment 2 Is On
2016/03/02 18:36:25 UPS Output Is On