Changing C7000 Enclosure G2 Power Redundancy Mode

Is there any impact to running blade servers when the Onboard Administrator changes the Power Redundancy Mode from Power Supply Redundant to AC Redundant.

 

I have 6 available power supplies in the enclosure, but want to make sure changing the configuration won't have any impact on the running blade servers.

 

Any advice would be appreciated. Thanks

2 REPLIES 2
Ing-Syst
Advisor

Re: Changing C7000 Enclosure G2 Power Redundancy Mode

If 3 power supplies are enough for your enclosure, you can switch mode online.

Casper42
Respected Contributor
Solution

Re: Changing C7000 Enclosure G2 Power Redundancy Mode

To Clarify, you need to check the Power Allocation screen. If your allocation is less than 3 supplies can provide, then it is safe to switch the mode online.