background:
issue:
applied solutions which all failed:
starting to think there is an issue not only with the hard drives as suggested in other posts here in the forum, but also if there might be any issues with the build-in broadcom nic?
there are currently running both lab and production blades in the system so tamering with it will be an issue, but updates to OA as well as all other ILO2 is something we concider but not have plans for at the moment
anyone have any ideas as how to solve this without bringing in a tech from HP (no, we don't have any guarantee or support left with this blade)
Solved! Go to Solution.
Here's what I would do.
Get the blade BIOS / FW upgraded to latest and greatest. - Using the latest SPP, run it from a USB memorystik, using the KVM cable. Meaning you must be in front of the server, at least for as long as it take you to connnect the cable, and you will have to remove it later.
Run a full system diagnostics, at least 1 complete/full loop, if time and patients allow, let it run for a few days.
Do check the suvey for memory errors: recoverable memory error threshold exceeded - this particular failure, I have seen several times. You will see it only in the survey, and the failure LED is flashing. You do not see these failures in the IML nor during system test (Insight Diagnostics), and I have seen this result in unstable servers.
Do consider to set the BIOS and possible the ILo to default - Use the BIOS setup utility (F9(BSU)) this will not clear the IML.
If you have any entries in the IML. Fix the problem, and mark all entriesas repaired - do not cler the IML.
The ILo i also recommend to reset, from the F8 prompt - This reset do not affect Accounts AFIK.
Sure, you could consider to upgrade the OA as well.
Some general issus when using Browser GUI's
Incompatible browsers being used - to old / to new.
Browser cache - Clear the browser cache.
Java Cache (when java is user) - Clear the Java cache.
BR
/jag

Use the SUV (Sorry not kvm but suv) cable.
The SUV cable you attach in the front of the server - 2 cables came with the enclosure.
Cable got a VGA connector and and 2 USB connectors.
So simply use any VGA monitor, a USB keyboard and mouse. You might be 1 USB port short. You can use a USB hub. Or as I sometimes do, start with the keyboad attached, then remove kb and connect mouse when needed.
You do need a USB connector for the memory stick.
Work for all C-class ProLiant blades.
If SPP still hang during boot, remove the FC HBA, if theres 1 installed.
BR
/jag

Good luck.
Remember - The monitor need power :)
br
/jag

so now the blade has been installed and configured as we want it and it runs perfectly...
running an ILO2-update so it has the same version as all other blades, which i have found out need to be done in steps..
so in order to make this post SOLVED this is what i have found out:
thanks to gregersenj for providing support
i hope this might help someone else, if you need more information don't hesitate and ask me please
Greate, good news :) and you're welcome.
FYI. the FW DVD is no longer used. It has been replaced by the SPP. and FW DVD 10.10 is outdated.
Latest OA Fw is 3.71. For the interconnect modules, you will hve to check individually.
BR
/jag

The iLO2 firmware update failure issue when using Internet Explorer browsers was fixed in iLO2 version 2.09. If you have older iLO2 versions, the workaround is to use FireFox instead of IE.