UPS_CONF

I am attempting to confingure the ups deamon to shut down after a certain time... however, i am unsure which variable controls which procedure. Delay or Timeout?!!

I'd ideally like to shutdown after an hour and a half without power?

an ideas?
5 REPLIES 5
Helen French
Honored Contributor

Re: UPS_CONF

This document will be helpful (TKB #UUPSKBRC00008714):

http://www1.itrc.hp.com/service/cki/docDisplay.do?docLocale=en_US&docId=200000068401378
Life is a promise, fulfill it!
A. Clay Stephenson
Acclaimed Contributor

Re: UPS_CONF

shutdown_delay_mins is the actual delay initiated from the loss of AC power to begin the shutdown.

A man ups_conf will tell you all of this. I must say that being able to set shutdown_delay_mins to 90 will require a very lightly loaded UPS or huge battery packs.
If it ain't broke, I can fix that.
A. Clay Stephenson
Acclaimed Contributor

Re: UPS_CONF

One other thing to consider is that even if your UPS will handle the load for 90+ minutes is that without power to HVAC systems will temperatures rise to dangerous levels?
If it ain't broke, I can fix that.
Kevin Daines
Advisor

Re: UPS_CONF

we have battery power for up to 2 hours, so that is not an issue. The maximum allowed in both timeout and delay is 15 mins though?

surly 30mins isn't the maximum allowed time on battery?

Darren Prior
Honored Contributor
Solution

Re: UPS_CONF

Hi,

Your ups may be able to cope with that length of battery time, but what happens if the power drops out for a 2nd time? I believe that's why the "traditional" values have been to supply power for 15 mins.

There is a patch however for ups_mond that increases the max value to 1092 mins. The patch is PHCO_29054 (11.0), PHCO_27828 (11i) and I strongly urge you to read the patch text first as it discusses ups types that this applies to.

regards,

Darren.