ProLiant Servers (ML,DL,SL)
1822548
Members
2750
Online
109642
Solutions
Forums
Categories
Company
Local Language
юдл
back
Forums
Discussions
Forums
- Data Protection and Retention
- Entry Storage Systems
- Legacy
- Midrange and Enterprise Storage
- Storage Networking
- HPE Nimble Storage
Discussions
Forums
Discussions
Discussions
Discussions
Forums
Forums
Discussions
юдл
back
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
- BladeSystem Infrastructure and Application Solutions
- Appliance Servers
- Alpha Servers
- BackOffice Products
- Internet Products
- HPE 9000 and HPE e3000 Servers
- Networking
- Netservers
- Secure OS Software for Linux
- Server Management (Insight Manager 7)
- Windows Server 2003
- Operating System - Tru64 Unix
- ProLiant Deployment and Provisioning
- Linux-Based Community / Regional
- Microsoft System Center Integration
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Blogs
Information
Community
Resources
Community Language
Language
Forums
Blogs
Topic Options
- Subscribe to RSS Feed
- Mark Topic as New
- Mark Topic as Read
- Float this Topic for Current User
- Bookmark
- Subscribe
- Printer Friendly Page
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО03-07-2006 01:26 PM
тАО03-07-2006 01:26 PM
240V ok?
Have a computer room in a really old building were only 240V/120V (Not 208V) power is available... just like at your house.
I see that DL380 G4's have a rated range of 100-240V with an acceptable input of 90-264V. The DL360 G4's have the same rating, but no mention of the "acceptable" limit.
Is it permissible to run these servers at 240V?
This is all run from a 20KVA UPS so large amperage inputs are not a problem. I would like to use some of HP's high voltage PDU's now, as we are moving to a new building in a couple years where 208V will be in abundance and don't want to buy a whole 'nother set of stuff.
I see that DL380 G4's have a rated range of 100-240V with an acceptable input of 90-264V. The DL360 G4's have the same rating, but no mention of the "acceptable" limit.
Is it permissible to run these servers at 240V?
This is all run from a 20KVA UPS so large amperage inputs are not a problem. I would like to use some of HP's high voltage PDU's now, as we are moving to a new building in a couple years where 208V will be in abundance and don't want to buy a whole 'nother set of stuff.
3 REPLIES 3
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО03-07-2006 05:21 PM
тАО03-07-2006 05:21 PM
Re: 240V ok?
I believe all the HP Proliant servers starting with G2's, and maybe even some G1's, all have 110 to 240 auto sensing power supplies. I would see no problem running the 360's at 240v. Since you are on a UPS, I assume the line is conditioned and protected so you should be ok.
To get the absolute official word, I would make the call to HP.
Steven
To get the absolute official word, I would make the call to HP.
Steven
Steven Clementi
HP Master ASE, Storage, Servers, and Clustering
MCSE (NT 4.0, W2K, W2K3)
VCP (ESX2, Vi3, vSphere4, vSphere5, vSphere 6.x)
RHCE
NPP3 (Nutanix Platform Professional)
HP Master ASE, Storage, Servers, and Clustering
MCSE (NT 4.0, W2K, W2K3)
VCP (ESX2, Vi3, vSphere4, vSphere5, vSphere 6.x)
RHCE
NPP3 (Nutanix Platform Professional)
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО03-07-2006 06:08 PM
тАО03-07-2006 06:08 PM
Re: 240V ok?
Yeah after reading a bit more, I'm beginning to think the "100-240V" rating is just an inclusive list of the 100,110,120,220,208,240 standards that are out there worldwide. The real range is some standard +/- percentage at each of those points.
I'll call hp tomorrow and post the results here.
(Come to think of it, I powered a Proliant 6500 from 240V years ago with no problems! I may have answered my own question?)
Thanks...
I'll call hp tomorrow and post the results here.
(Come to think of it, I powered a Proliant 6500 from 240V years ago with no problems! I may have answered my own question?)
Thanks...
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО03-08-2006 01:40 PM
тАО03-08-2006 01:40 PM
Re: 240V ok?
Yup. They said it's fine!