- Community Home
- >
- Servers and Operating Systems
- >
- HPE ProLiant
- >
- ProLiant Servers (ML,DL,SL)
- >
- Proliant DL 360G7 und USV
Categories
Company
Local Language
Forums
Discussions
Forums
- Data Protection and Retention
- Entry Storage Systems
- Legacy
- Midrange and Enterprise Storage
- Storage Networking
- HPE Nimble Storage
Discussions
Discussions
Discussions
Discussions
Forums
Forums
Discussions
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
- BladeSystem Infrastructure and Application Solutions
- Appliance Servers
- Alpha Servers
- BackOffice Products
- Internet Products
- HPE 9000 and HPE e3000 Servers
- Networking
- Netservers
- Secure OS Software for Linux
- Server Management (Insight Manager 7)
- Windows Server 2003
- Operating System - Tru64 Unix
- ProLiant Deployment and Provisioning
- Linux-Based Community / Regional
- Microsoft System Center Integration
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Community
Resources
Forums
Blogs
- Subscribe to RSS Feed
- Mark Topic as New
- Mark Topic as Read
- Float this Topic for Current User
- Bookmark
- Subscribe
- Printer Friendly Page
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО12-20-2018 06:47 AM - edited тАО12-20-2018 07:01 AM
тАО12-20-2018 06:47 AM - edited тАО12-20-2018 07:01 AM
Proliant DL 360G7 und USV
Hallo,
ich habe ein Problem mit einem DL360G7 Server. Und zwar habe ich bisher 2 USV's ausprobiert (eine APC 450 und eine V7 VC1500). Die APC war klar zu klein mit 280Watt, aber die V71500 mit 900 Watt sollte eigentlich ausreichen.
Mein Problem: beim Battreietest und bei einem simulierten Stromausfall schaltet die USV zwar auf Batteriebetrieb, aber der Server schaltet sofort ab. D.h. er l├дuft erst gar nicht auf Batterie. Batterien sind neu und auch voll geladen. Die Software zeigt alle Daten korrekt an. Laut Monitor hat der Server eine Last von 160-200 Watt und eine Batterielaufzeit von ca 45 Minuten. Trotzdem ist der Server sofort weg, sobald die USV auf Batteriebetrieb umschaltet. Kann das an zu langer Latenzzeit liegen? Laut Hersteller hat die USV eine Umschaltzeit von 6 -10 ms. Kann es an einer Einstellung im BIOS liegen? Bin leider kein Fachmann und wei├Я mir nicht zu helfen.
Sorry thought I was in a German message board.
My problem: I got a UPS V7-VC1500 fort the above server. According to the software monitor the battery is full, the load ist about 160-200 watts and the server should run for 45 min on battery. But as soon as I do a battery test or a simulated power fail the server crashes imediately even if the UPS switches to battery. I have no idea why. Can it be that the latency is to high? Is there anything to change in the BIOS of the server? Thanks for any help.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО12-20-2018 07:26 AM - last edited on тАО12-20-2018 10:12 PM by Vajith V
тАО12-20-2018 07:26 AM - last edited on тАО12-20-2018 10:12 PM by Vajith V
Re: Proliant DL 360G7 und USV
Also ich hatte schon ├╢fters USVs, wo der interne umschalter defekt war.
Dann zeigen die alles OK an und wenn der Strom ausf├дllt geht trotzdem nichts mehr.
Schon mal einen anderen starken Verbraucher drangesteckt (Heizl├╝fter, Halogenstrahler) und gepr├╝ft, ob die auf Batteriebetrieb funktionieren?
Im Server BIOS kann man nichts dazu einstellen.
Normalerweise sind die USVs schon so gebaut, da├Я die umschaltzeit f├╝r den Server kurz genug ist.
Google Translation
I had often UPSs where the internal switch was broken.
Then they show everything OK and when the power goes out, nothing works anymore.
Have you ever plugged another strong consumer (fan heater, halogen spotlight) and checked whether they work on battery power?
You can not set anything in the server BIOS.
Normally, the UPSs are already built so that the switching time for the server is short enough.

- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО12-20-2018 07:42 AM - last edited on тАО12-20-2018 10:13 PM by Vajith V
тАО12-20-2018 07:42 AM - last edited on тАО12-20-2018 10:13 PM by Vajith V
Re: Proliant DL 360G7 und USV
Also mit der von APC hatte ich das schon probiert und einen Win7 Rechner drangeh├дngt. Da hat es funktioniert. Daher dachte ich, dass die f├╝r den Server einfach nur zu unterdimensioniert ist. Hatte dann aber mit der neuen und gr├╢├Яeren genau das gleiche Problem. Mit der habe ich aber noch nicht getestet, ob ein anderer Verbraucher geht. Kann ich leider erst nach den Ferien testen.
Google Translation
So with the APC I had already tried that and hung a Win7 computer. It worked there. Therefore, I thought that for the server is just too undersized. Had then but with the new and larger exactly the same problem. But I have not tested it yet with the other consumer. Unfortunately, I can only test after the holidays.