HP R5000 UPS (Shutdown Parameters)

 
MaartenLeyman
Occasional Visitor

HP R5000 UPS (Shutdown Parameters)

Hello,

I have a question about the shutdown parameters of HP r5000 ups.

 

 

As you can see the UPS was starting to shutdown after 5 minutes (300seconds)

Why is not shutdown after 20% battery?


Or does it shutdown after 300seconds or 20% battery?

 

2 REPLIES 2
gsb_2
Regular Advisor

Re: HP R5000 UPS (Shutdown Parameters)

I called HP on this and he said to ignore the second field( the 20% one) The two fields are separate. There really should be the word "or" between the two statements.

 

Set the Load Segment 1 and Load Segment 2 fields to a really high number. I have mine set to 12000 seconds(over 3 hours)

 

So now my UPS will stay up for 12000 seconds or until the battery goes below 20%.

dalton_cm
Frequent Visitor

Re: HP R5000 UPS (Shutdown Parameters)

Thanks for clearing that up, I was caught by surprise when ours initiated the 5 minute countdown immediately.  It is extremely unfortunate that the wording on the page (or in the help) doesn't clarify things.  As you stated, an "or" would be a huge help.