Servers - General
1849031 Members
4856 Online
104041 Solutions
New Discussion

Issues with UPS NMC AF465A not setting static IP adress...

 
SOLVED
Go to solution
deejinoz
Occasional Advisor

Issues with UPS NMC AF465A not setting static IP adress...

Hi,

The network management module is not allowing us to change it IP adress from dynamic to static. Whenever we set the static IP, in the NMC Web management interface, it shows the following message "If you have modified the IP configuration, you have to reset communication on System Settings." So, we go to System and hit the "Reset Communications" button. The UPS disappears off the network for a couple of minutes then reappears with the same DHCP address again.

The NMC has been replaced, as well as the entire UPS (which was to address another issue, where the NMC couldn't communicae with the UPS). Whilst the new NMC is able to communicate with the new UPS and appears to function correctly, the IP address will not change from dynamic to static, even on this new NMC.

I have had several cases open, with HPE support, over the last month or so, while we replace and test the entire UPS system and we are still no closer to fixing this issue. Last night, the HPE support engineer asked me to upload the logs from the NMC, which ammounted to about a total of 50 lines of events that showed virtually nothing going on, on the UPS, and certainly no errors related to the issue. We are now waiting to hear from engineering.

About the UPS:
UPS Name : HP R/T3000 HV INTL UPS
UPS Part Number : J2R04A
UPS Serial Number : nnnnnnnnnn
UPS Firmware Revision : 01.08.0009
Communication Board Firmware Revision : Not Available

About the NMC:
HPE UPS Network Module
Card Firmware revision : 1.08.004 (Firmware not updated to the latest, on recommendation of HPE support!)
Card Part Number : AF465A
Card Technical Level : 09
Card Hardware Revision : BG
Card Serial Number : xxxxxxxxxx
Card Ethernet Mac Address : xx:xx:xx:xx:xx:xx
Card Ethernet Speed : 100 MBit

About the computer I'm managing it from:
Windows Server 2016
Chrome Version 70.0.3538.77 (Official Build) (64-bit)
OS is running as a VMware guest on an HP ProLiant G9 DL180 server with HPE Customized Image ESXi 6.5.0 Update 1 version 650.U1.10.1.5 released on October 2017 and based on ESXi 6.5.0 Update 1 Vmkernel Release Build 6765664.
The DHCP Server is also running on a VMware guest, on the same host and is serving other DHCP cllients on the network, including other HPE rack & power systems (smart PDUs) without any issues.

Anybody else experienced this before or have any suggestions?

5 REPLIES 5
Rafi786
HPE Pro

Re: Issues with UPS NMC AF465A not setting static IP adress...

Good Day,

Thanks for posting the issue here.

I heard from HPE support team that there is a support case submitted for this issue. This issue is being investigated further and support team will get in touch with you.

 

Mohd Rafiuddin
I work for HPE. The comments in this post are my own and do not represent an official reply from the company. No warranty or guarantees of any kind are expressed in my reply.

Accept or Kudo

Bunsol
HPE Pro

Re: Issues with UPS NMC AF465A not setting static IP adress...

Hi Dee,

Hope this helps you. On the terminal emulation session screen running on the host computer enter the Network configuration settings and follow the below steps:-

HP NETWORK MANAGEMENT MODULE
-----------------------------------------------------------------------------
1 : Reset
2 : Network configuration
3 : Set Login Password to Default
4 : Return to Default Configuration
0 : Exit
-----------------------------------------------------------------------------


-----------------------------------------------------------------------------
Network settings
-----------------------------------------------------------------------------
1 : Read Network settings
2 : Modify Network settings
3 : Set Ethernet speed
0 : Exit
-----------------------------------------------------------------------------

For each of the following questions, you can press <Return> to select the value
shown in braces, or you can enter a new value.

Should this target obtain IP settings from the network?[N]
N
Static IP address [xxx.xxxx.x]?
xx.xx.xx.x
Static IP address is xx.xx.xx.x 
Subnet Mask [255.xxx.x.x]?
255.xxx.xxx.x 
Subnet Mask is 255.xxx.xxx.x
Gateway IP address [0.0.0.0]?
xx.xx.xx.xxx 
Gateway IP address is xx.xx.xx.xxx 
Wait during your new configuration is saved ...
Reset the card to take into account the new configuration.


-----------------------------------------------------------------------------
Network settings
-----------------------------------------------------------------------------
1 : Read Network settings
2 : Modify Network settings
3 : Set Ethernet speed
0 : Exit
-----------------------------------------------------------------------------
File RAM0/ConfigurationData.xml created with 18451 bytes
File RAM0/ConfigurationData.xml written in Flash with 18451 bytes
Exit

 

-----------------------------------------------------------------------------
HP NETWORK MANAGEMENT MODULE
-----------------------------------------------------------------------------
1 : Reset
2 : Network con
3 : Set Login Password to Default Menu :
4 : Return to Default Configurationintenance Menu :
0 : Exit
******


-----------------------------------------------------------------------------

 

-----------------------------------------------------------------------------------------------------------------------------------
Reset
-----------------------------------------------------------------------------
2 : Network configuration
3
1 : Restart the card from the boot
4 :
0 : Exitt Configuration
------------------------------------------------------------------------------------------------------------------------------------------------------


RAM autotest SUCCESS.
3 :

Commercial reference : xxxxxx
0 :
Kitting technical level : 09----------------------------
Kitting revision : BG--------------------
Ethernet MAC Address : xx:xx:xx:xx:xx:xx 
Netw
Serial number : xxxxxxxxx 
MA

PHY autotest SUCCESSx:xx:xx 
FLASH autotest SUCCESS.
Mode : DHCP
-----------------------------------------------------------------------------
HP NETWORK MANAGEMENT MODULE
USER APPLICATION VERSION :x.xx.xxx
-----------------------------------------------------------------------------
Network connection with static IP mode...

 

 

Regards,

Bunsol


If you feel this was helpful please click the KUDOS! Thumbs below!

I work at HPE
HPE Support Center offers support for your HPE services and products when and how you need it. Get started with HPE Support Center today.
[Any personal opinions expressed are mine, and not official statements on behalf of Hewlett Packard Enterprise]
Accept or Kudo
deejinoz
Occasional Advisor

Re: Issues with UPS NMC AF465A not setting static IP adress...

Hi Bunsol,

The case is not related to setting the IP via a terminal session. The case is specifically related to setting the IP via the NMC Web interface. Kindly re-evaluiate your response accordingly.

Thanks.

David

Bunsol
HPE Pro

Re: Issues with UPS NMC AF465A not setting static IP adress...

Hi Dee,

The only option will be through the Serial port. If there are issues of having a serial port connecting device or any other issue for connectivity then please log a support ticket with us if no ticket is logged. If a ticket is logged then we request you to continue with that to get this resolved.

 

Regards,

Bunsol


If you feel this was helpful please click the KUDOS! Thumbs below!

I work at HPE
HPE Support Center offers support for your HPE services and products when and how you need it. Get started with HPE Support Center today.
[Any personal opinions expressed are mine, and not official statements on behalf of Hewlett Packard Enterprise]
Accept or Kudo
deejinoz
Occasional Advisor
Solution

Re: Issues with UPS NMC AF465A not setting static IP adress...

So, HPE have confirmed that there is a known bug in this devices firmware, whereby you will have problems and most likely not be able to set a static IP address for the device, through its Web interface. The only way you can reliably set this device to use a static IP address is through a direct serial console session. HPE have also confirmed that they have no expected fix for this bug at this time.

Not the kind of quality one would have expected from HPE, in the past. But, unfortunately, no real surprise, these days.