Re: R12000 UPS REPO Alarm

 
Charles Klima
Occasional Advisor

R12000 UPS REPO Alarm

Our new used R12000 UPS shuts down after initial power up of electronic modules. There are two alarms: the bypass alarm, which is OK, and the Remote Emergency Power Off (REPO) alarm which is not OK, and I believe is the problem. It indicates that the UPS was powered off remotely. There is no remote switch hooked up. This unit is purely for testing batteries and electronics modules, so the only external connection is the power input. I've been researching how to disable this REPO error internally through the control panel but the manuals don't cover this. Any help would be appreciated.
3 REPLIES 3
Johan Guldmyr
Honored Contributor

Re: R12000 UPS REPO Alarm

Hi, maybe there's something stuck in the port causing it to be triggered?
Charles Klima
Occasional Advisor

Re: R12000 UPS REPO Alarm

Thank you for the reply. I was able to get rid of the REPO alarm. There are two wire terminals in rear of the R12000 where an emergency switch is supposed to be connected. We jumped the terminals with a wire and now the REPO error has disappeared, even when the wire is disconnected. It was probably a stuck relay. Thanks again, closing thread.
Charles Klima
Occasional Advisor

Re: R12000 UPS REPO Alarm

I found the solution. It is stated in my reply to the first responder.