BladeSystem - General
1752781 Members
6586 Online
108789 Solutions
New Discussion юеВ

Re: config loading on hp c7000

 
Johan Huysmans
Occasional Contributor

config loading on hp c7000

The "SET EBIPA" section of my config file is loaded very slowly. All the other sections are on a more normal speed.

Is this normal or can this be tuned?

thx!
4 REPLIES 4
Johan Huysmans
Occasional Contributor

Re: config loading on hp c7000

It takes 20 seconds to perform following command:

SET EBIPA SERVER 192.168.251.70 1


During the run it also outputs following lines:
Successfully set device (iLO) bay # 1 to IP address 192.168.251.70
A possible duplicate IP address was found on the network: 192.168.251.70.
A possible duplicate IP address was found on the network: 192.168.251.71.
A possible duplicate IP address was found on the network: 192.168.251.72.
A possible duplicate IP address was found on the network: 192.168.251.73.
A possible duplicate IP address was found on the network: 192.168.251.74.
A possible duplicate IP address was found on the network: 192.168.251.75.
A possible duplicate IP address was found on the network: 192.168.251.76.
A possible duplicate IP address was found on the network: 192.168.251.78.
A possible duplicate IP address was found on the network: 192.168.251.79.
A possible duplicate IP address was found on the network: 192.168.251.80.
A possible duplicate IP address was found on the network: 192.168.251.81.
A possible duplicate IP address was found on the network: 192.168.251.82.
A possible duplicate IP address was found on the network: 192.168.251.83.
A possible duplicate IP address was found on the network: 192.168.251.84.

For the IP addresses to be assigned EBIPA must be enabled.


Is this normal?
The Brit
Honored Contributor

Re: config loading on hp c7000

Hi Johan,

Yes, I believe this is normal.

When you modify or apply an IP address in EBIPA, and click the APPLY button, the OA performs an update on all of the device bays, even though they may not have changed.

The sad part is that it doesn't seem to have enough smarts to recognize that the "duplicate" is the actual bay it is currently trying to update. i.e it tries to set IP = X on the device bay which already has IP = X, and announces that it is a duplicate. It will give this response for every bay where the IP is not changing.

Go figure.

Dave.
Johan Huysmans
Occasional Contributor

Re: config loading on hp c7000

thx for the info!

Is there any chance it will be solved in a future firmware version?
Cederberg
Honored Contributor

Re: config loading on hp c7000

Yes it seems to be fixed in OA FW version 3.00

The method used to determine duplicate EBIPA IP addresses within OA 2.60 and earlier has been found to be unreliable and at times indicates duplicate IP addresses that were in fact not duplicate, thus duplicate IP address checking has been removed from the OA 3.00.