I have a configuration of 2 x 3 phase power attached to 4 enhanced enclosures. A couple of days ago we had the left side of the rack power down. When we noticed and looked at the rack, all the PSU's looked on, the scalable bus bars and power enclosures all lights were on, but all the blades had no lights, not even a standby light. Reseating the blades did make them come back up. But I'm trying to find out why it happened. How do you check on P-Class what the redundancy is set to on? I have attached a serial connection and collected the below. Any advise would be greatly appreciated. If it helps we have a mixture of BL25p and BL45p in the rack. we are alo running 2.4 f/w on all enclosures.

 

LQQQQQQQ REDUNDANCY KEY QQQQQQQQQQK                                      
XXXXX = NOT PS REDUNDANT          X                                      
XXXXX = NOT BUS BAR REDUNDANT     X                                      
XXXXX = NOT PWR. ENCL. REDUNDANT  X                                      
MQQQQQQQQQQQQQQQQQQQQQQQQQQQQQQQQQJ                                      
 ICMB   A    BOTH   B                                                    
 E410  1174   240     0  Z-CLASS CHASSIS <<<<<<< DO WE KNOW WHY B IS SET 0
 E22F   908   240   454  Z-CLASS CHASSIS                                 
 992F   681   240   908  Z-CLASS CHASSIS                                  

 CCF0   681   240   908  Z-CLASS CHASSIS          
 4CBB >8721<      >8721< POWER CHASSIS            
 3B24 >8721<      >8721< POWER CHASSIS            

 

Many Thanks

 

Koopa79

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

2 REPLIES 2
Louis Henninger_1
Regular Advisor

Re: P-Class Power questions .... PLEASE HELP!!!!

question: Are all power zones set the same?

 

Louis

Koopa
Frequent Advisor

Re: P-Class Power questions .... PLEASE HELP!!!!

I believe that on 2.4 f/w everything gets set to zone 3, which is obviously something you can't normally set by the back of the enclosures.