Hello,

I am fixing to design a new computer room which will store some L2000 machines. I would like to know if anyone can tell me how many BTU's the HP9000 L2000 server puts out?

Thanks.
2 REPLIES 2
Joshua Scott
Honored Contributor
Solution

Re: BTU output on L2000

The Maximum Heat Dissipation for the L2000 is 4380 BTUs/hour.
Typical output is 3000 BTUs/hour

-Josh
What are the chances...
Thayanidhi
Honored Contributor

Re: BTU output on L2000

Hi,

Maximum configuration Rp54xx
Watts: 1283
Kcal/Hr:1104
BTU/Hr: 4380
Tons of refrigration required: 0.37

The formula is

├в ┬в Watts x (0.860) = kcal/hour
├в ┬в Watts x (3.414) = Btu/hour
├в ┬в Btu/hour divided by 12,000 = tons of refriger