- Community Home
- >
- Servers and Operating Systems
- >
- Legacy
- >
- HPE 9000 and HPE e3000 Servers
- >
- Re: BTU Rating for a UPS
Categories
Company
Local Language
Forums
Discussions
Forums
- Data Protection and Retention
- Entry Storage Systems
- Legacy
- Midrange and Enterprise Storage
- Storage Networking
- HPE Nimble Storage
Discussions
Discussions
Discussions
Discussions
Forums
Forums
Discussions
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
- BladeSystem Infrastructure and Application Solutions
- Appliance Servers
- Alpha Servers
- BackOffice Products
- Internet Products
- HPE 9000 and HPE e3000 Servers
- Networking
- Netservers
- Secure OS Software for Linux
- Server Management (Insight Manager 7)
- Windows Server 2003
- Operating System - Tru64 Unix
- ProLiant Deployment and Provisioning
- Linux-Based Community / Regional
- Microsoft System Center Integration
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Community
Resources
Forums
Blogs
- Subscribe to RSS Feed
- Mark Topic as New
- Mark Topic as Read
- Float this Topic for Current User
- Bookmark
- Subscribe
- Printer Friendly Page
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО09-17-2003 01:19 AM
тАО09-17-2003 01:19 AM
BTU Rating for a UPS
WE have a 42Kw UPS to be installed in the Server room. Does anyone know how to calculate the BTU rating for a UPS?? I could not get any details from the web site ( Its a BPC Power pro RT)
thanks
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО09-17-2003 01:58 AM
тАО09-17-2003 01:58 AM
Re: BTU Rating for a UPS
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО09-17-2003 03:02 AM
тАО09-17-2003 03:02 AM
Re: BTU Rating for a UPS
I'm afraid I don't know the answer to your question, but I'm assuming that you need to know the BTU rating so that you can calculate how much extra cooling is required for your server room. The BTU (British Thermal Unit) is a unit of energy, kW is a unit of power.
The following website has a conversion factor between kW and BTU/hr:
http://www.coxhardware.com/usefulinfo/charts/3a_engtbl.htm
which shows that 42Kw ~143000 BTU/hr
There's also some useful info on BTU and conversion here: http://www.eia.doe.gov/kids/btudef.html
regards,
Darren.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО09-17-2003 03:22 AM
тАО09-17-2003 03:22 AM
Re: BTU Rating for a UPS
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО09-18-2003 06:54 AM
тАО09-18-2003 06:54 AM
Re: BTU Rating for a UPS
-Josh
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО09-23-2003 07:08 AM
тАО09-23-2003 07:08 AM
Re: BTU Rating for a UPS
What you don't say is the efficiency of the UPS and that is really the crux of the problem. Modern UPS's typically have an efficiency of 93-96%. Let's use 95% as a good round value (and the efficiency typically also varies as a function of fraction of rated load).
43 KW(out) / .95 = 45.3 KW(in)
The difference between input power and output power 45.3 KW - 43 KW = 2.3KW is the power that is dissapated as heat and that is your additional cooling load -- at full load.
2.3 KW X 3413 BTU / HR - KW = 7850 BTU/HR
You therefore need to make sure that your existing HVAC unit can handle the additional 7850 BTU/HR thermal load. If the efficiency rating is known, you can , of course, may more refined calculations but 95% should be "close enough".