Servers - General
1854671 Members
14435 Online
104102 Solutions
New Discussion

Query: HP R5000 UPS Issue

 
AbeAyende
Frequent Visitor

HP R5000 UPS Issue

Site wiring fault warning always present, the wiring was calculated for continuous use @30 amps, the earth is free of voltage, test reading was 150 mV (. 150 V), casing also to earth bus, this is a separate earth designed for the server room and the fault keeps showing. Any suggestions to resolve the issue?

Thanks kindly
Abe Ayende
Electrician
4 REPLIES 4
support_s
System Recommended

Query: HP R5000 UPS Issue

System recommended content:

1. HP UPS R5000 Installation Instructions

2. HPE UPS R5000 User Guide

 

Please click on "Thumbs Up/Kudo" icon to give a "Kudo".

 

Thank you for being a HPE valuable community member.


Accept or Kudo

AbeAyende
Frequent Visitor

Re: Query: HP R5000 UPS Issue

Greetings and thank you for your response, but this information was already at our disposition and does not address the alarm code # 194 as the UPS is claiming that there is an issue with the building wiring.
Facts
1. The UPS is configured for a 208V input, meaning 2 phases and an earth cables. NO Neutral.
2. Building is properly grounded, test confirms no voltage neutral to ground.
3. No where in the documentation or support forum, or HPE site does it mention the proper fix for this alarm #194.

Really appreciate any guidance and support you can provide.

Thanks kindly
Abe
Sham82
HPE Pro

Re: Query: HP R5000 UPS Issue

Hello @ AbeAyende,

Thank you for your post.

Alarm code 194 is - "The voltage difference between ground and neutral is below 30V."

Since when are you facing this issue?
What is the Impact?
Have you tried a different wall outlet?


https://support.hpe.com/hpesc/public/docDisplay?docId=c02945229&docLocale=en_US
please refer to:

Page 31 - Enables or disables site wiring fault alarm. The default is Disabled
page 40 - Alarm troubleshooting

 

Regards
HPE



I work at HPE
HPE Support Center offers support for your HPE services and products when and how you need it. Get started with HPE Support Center today.
[Any personal opinions expressed are mine, and not official statements on behalf of Hewlett Packard Enterprise]
Accept or Kudo
support_s
System Recommended

Query: HP R5000 UPS Issue

Hello,

 

Let us know if you were able to resolve the issue.

If you are satisfied with the answers then kindly click the "Accept As Solution" button for the most helpful response so that it is beneficial to all community members.

 

 

Please click on "Thumbs Up/Kudo" icon to give a "Kudo".


Accept or Kudo