Re: R5500 UPS - Loss of redundant communication

 
Eivind Lunde
Occasional Contributor

R5500 UPS - Loss of redundant communication

Hello
I have a R5500 UPS with an ERM module, connected to a server running the HP UPS Management Module software.

The software has started reporting a "critical alarm" saying "Loss of redundant communication".
What does this mean?
Could it be that the ERM module is not correctly installed?
4 REPLIES 4
Eivind Lunde
Occasional Contributor

Re: R5500 UPS - Loss of redundant communication

The eventlog says the condition clears after a while then reappears, so it is not a permanent condition.
neilbo
Occasional Advisor

Re: R5500 UPS - Loss of redundant communication

Has anyone found an answer to this? I have the same issue.
Helmut Moltke
Advisor

Re: R5500 UPS - Loss of redundant communication

Same here.

Ingenious
New Member

Re: R5500 UPS - Loss of redundant communication

When I did a search on this problem all I found was your post of a year or so ago.

 

Here is the answer:

Make sure you specify the first UPS's IP, and the second UPS on all your servers' Agent software  is set to No Server (Management Sever 1 and 2) otherwise you get this error all the time . This setting is for redundant UPS setup.

 

Other Details:

On the UPS look for servers with RU error - this means they are communicating with more than one UPS...

RU—The agent is communicating with both UPSs and

both UPSs have normal status.

AS—The agent is communicating with the management

module.